ask the electrician
Electrician Training Electrical Certification wiring recessed light fixtures Electrical Wiring Electrical Troubleshooting and Electrical Repairs wire outdoor light fixture Home Electrical Wiring Diagrams
wiring home generator and transfer switch wiring a 220 volt range cord outlet Wiring for GFCI Outlets Wiring Outlets and a Switched Outlet Wiring and Installing Ceiling Fans and Remote Controls wire dimmer switch wiring diagrams for switches wiring a dryer cord and 220 outlet circuit breaker panel
Electrical Wire and Cable


Repair a GFI Outlet Circuit


How can I fix a problem with my GFCI outlet circuit? How to Troubleshoot and Repair GFI Outlet Circuit Wiring.

© By:


Electrical Wiring Video



Home Electrical Wiring Videos about this Topic and More

Check out my YouTube Channel, and Subscribe!



Learn more with my Home Electrical Video Course:

Basic Home Electrical Wiring by Example

Steps for Testing a GFCI Outlet Circuit
Electrical Question #1: How can I fix a problem with my GFCI circuit?
I have a problem with the GFCI circuits in my home.

Thank you for your advice.
Jerry

This electrical wiring question came from: Jerry, in NY, New York.

Electrical Question #2:

This electrical wiring question came from Ray in Sulphur, Louisiana

Electrical Question #3:

This electrical wiring question came from Rick, a Homeowner in Eagan, Minnesota.

Dave’s Reply:
Thank you for your electrical wiring questions.

Troubleshoot and Repair GFCI Outlet Circuit Wiring

electrical troubleshooting GFCI outlet

How to Test a GFI Circuit

When the GFI circuit seems to be partially working or not working at all here are some things to double check to get the GFCI working again.

  1. Check for Loose Wires
    Make sure there are no loose wires within the circuit, especially the white neutral wire.
  2. Incoming Power Source: The LINE
    Make sure the incoming power source to the GFCI outlet are attached to the LINE side as indicated on the back of the receptacle.
  3. Outgoing Power Source: The Load
    Make sure the outgoing circuit wiring is connected to the LOAD side of the GFCI Outlet.
  4. LINE and LOAD Wiring
    Both the black and white wires must be connected separately into the appropriate terminals of the LINE and the LOAD side of the GFCI Outlet or GFI Receptacle.
  5. A Bad GFI
    If the wiring connections are correct and the circuit voltage is normal then the GFCI outlet may be faulty and should be replaced.
  6. Checking the Circuit Polarity
    The integrity of the GFI circuit wiring may be tested for voltage by temporarily removing the GFCI outlet and splicing the wires through and then testing the voltage and polarity at each receptacle outlet of the same circuit. If the voltage readings and polarity test is normal then the GFCI is faulty or the connections to the GFCI were incorrect.
  7. Plug-In Circuit Analyzer
    A plug in circuit analyzer will be helpful to determine the correct wiring of the circuit and help detect circuit faults.

Important Note about Ground Fault Circuit Interruption:
Both GFI and GFCI are basically the same and both provide protection against ground faults by interrupting the electrical circuit by sensing voltage that passes to a ground source.

See More about Electrical Wiring for a GFCI Outlet


The following may also be helpful for you:


electrical wiring book

A Complete Guide to Home Electrical Wiring

Be sure to get your copy of my BIG Book:
Perfect for Homeowners, Students and Electricians
Includes:
Home Electrical Wiring - Room by Room
120 Volt Circuits
240 Volt Circuits
Multi-Wired Circuits
Wiring Methods for Installing Home Electrical Circuit Wiring
Electrical Codes for Home Electrical Wiring
....and much more.




Be Careful and Be Safe - Never Work on Energized Circuits!
Consult your Local Building Department about Permits and Inspections for all Electric Wiring Projects.

More articles about Electrical Repair and Home Electrical Wiring:

« Previous Next »

Electrical Troubleshooting Lost Outlet Power

Is it Safe to Replace Circuit Breakers in a Breaker Box?



FAQs Frequently Asked Questions and Comments

6 Responses to “Repair a GFI Outlet Circuit”
  1. Dave Rongey says:

    Hi Tom,
    From what you have described here is the process that I would take: Make sure the damaged hedge trimmer cord is unplugged. Reconnect any wiring and reinstall any receptacles and cover plates that have been opened. Then go to the electrical panel and look for the circuit breaker for the outside receptacles, switch the breaker all the way into the Off position, and then back into the On position. This will reset the circuit breaker and should restore power to the outdoor receptacle circuit. Double check and test the GFCI receptacle to make sure it is functioning correctly.
    I hope this helps,
    Dave

  2. Tom Williams says:

    I was trimming my hedges when I inadvertently cut the extension cord with the hedge trimmer. This shorted out the outlet where the extension cord was plugged in. However the outlet is a GFCI type. I disconnected the three wires attached to the receptacle and tested the hot and neutral with my tester but there was no voltage. The other outside receptacles have no power either. Does this mean I have to replace the circuit breaker connected to the three GFCI outlets?

  3. Dave Rongey says:

    Hi Ed,
    Try replacing the GFI just in case you have a defective one. If that does not help then I suspect there is a problem within the circuit wiring which will need to be tracked down. Start by turning off the circuit power and inspecting all of the other outlet boxes, remove the outlets or devices, and look for anything that may cause moisture or a path between circuit components and the ground system. With situations like this I have even found that insects that nest into these areas which in some cases is enough to cause nuisance tripping of the GFI.
    Dave

  4. Ed Drager says:

    I have a new home and the two GFI on the exterior of the home has always worked. One of the GFI’s has the test buttons on it and the other one does not. I have tried replacing the test receptacle and it will not work either. I have a load to the test receptacle and I can not trip either test buttons. I even replaced the other receptacle and that did not work. I am thinking that I might have gotten a bad GFI to replace the old one.

  5. Dave Rongey says:

    Hi Stan,
    I would search for a GFCI outlet that has tripped OFF. Begin looking on the porches, laundry room or the garage and I’ll bet you will find a GFCI outlet. If you locate a GFI outlet that is not tripped then make sure to press the TEST button to manually test it, and if it does not trip then the GFI outlet is at fault and needs to be replaced, and this will most likely solve the problem with the other outlets that are not working.
    Dave

  6. Stan says:

    Just purchased a home and it was inspected with all outlets working. Sometime during the past few weeks all 5 exterior outlets have stopped working. I have checked every outlet and switch in the house. The only ones not working are these 5. I None of these outlets are breakered and I cannot figure out which circuit breaker on the main panel feeds them. Any idea of what to do next?